Thread: Picked the wrong setting for "SOV" and Xl824 is backwards

  1. #1
    Junior Member

    User Info Menu

    Picked the wrong setting for "SOV" and Xl824 is backwards

    Just installed the XL824 and little did I know that trane calls the reversing valve the SOV VALVE. I picked heat and that must have been the wrong one. When I call up the heat the A/C cuts in and when I call up the A/C the heat cuts on. How do I get back into setup to change this? All replies are appreciated!!! I'm in a pinch. Thanks

  2. #2
    Administrator

    User Info Menu

    Look at page 24 and 25 of the PDF link http://www.bayareaservice.com/store/XL824_Install.pdf you need to change the SOV operation

  3. #3
    Junior Member

    User Info Menu

    ok doing that now. Thanks

  4. #4
    Junior Member

    User Info Menu

    Quote Originally Posted by Thermostat View Post
    Look at page 24 and 25 of the PDF link you need to change the SOV operation
    what my problem is that I cant get back into the "installer setup" to make the change. Thanks alot for helping so far. It seems as if the
    homeowner setup is all I can access. There is no option for me to change the installer settings. That I can see anyhow. Grrr. lol

  5. #5
    Junior Member

    User Info Menu

    I found it. Thanks guys!

  6. #6
    Administrator

    User Info Menu

    What were the steps that you had to take to make the change?