Thread: Nest (3rd Gen) thermostat gives error code E104

  1. #7
    Junior Member

    User Info Menu

    Quote Originally Posted by Thermostat View Post
    All of the other wires that connect from the Nest to the ECW will stay as there were. Only the G wire changes. The C terminal on the ECW will now have 2 wires.
    I received the PAM-1 relay (from Amazon) and tried to understand the corresponding wiring (colors) for correct connections... Here's what I'm thinking:

    Pam-1 white / 0V > C terminal on NCM-300
    Pam-1 red / 24V > G terminal on NCM-300
    Pam-1 black / 120V > R terminal on NCM-300




    Pam-1 blue / C > G wire from Nest thermostat.
    Pam-1 orange / N.O > What does this connect to?
    Pam-1 yellow / N.C > What does this connect to?

    Please correct me if I'm wrong.... Appreciate any/every help!

    Thank you

  2. #8
    Administrator

    User Info Menu

    Pam-1 white / 0V > C terminal on NCM-300
    Pam-1 red / 24V > G terminal from Nest
    Pam-1 black / 120V > Place a wire nut on this wire

    Pam-1 blue / C > R terminal on NCM-300
    Pam-1 orange / N.O > G terminal on NCM-300
    Pam-1 yellow / N.C > Place a wire nut on this wire

  3. #9
    Junior Member

    User Info Menu

    Quote Originally Posted by Thermostat View Post
    Pam-1 white / 0V > C terminal on NCM-300
    Pam-1 red / 24V > G terminal from Nest
    Pam-1 black / 120V > Place a wire nut on this wire

    Pam-1 blue / C > R terminal on NCM-300
    Pam-1 orange / N.O > G terminal on NCM-300
    Pam-1 yellow / N.C > Place a wire nut on this wire
    Great, I wired it up last night and it didn't make any difference... After making the above suggested connections via the PAM-1 relay, these are the connections that went to the "thermostat zone-2" on NCM-300:

    1. White (from PAM-1 relay) & Blue wire (common from Nest thermostat) ----> C on NCM-300
    2. White wire (from Nest thermostat) ----> W/E on NCM-300
    3. Yellow wire (from Nest thermostat) ----> Y on NCM-300
    4. Blue (from PAM-1 relay) & Red wire (from Nest thermostat) ----> R on NCM-300
    5. Orange (from PAM-1 relay) ----> G on NCM-300

    I still think I might've wired it somewhat incorrectly and the reason is (1) & (4) from above.. Does that sound right to you?

    Looking at the "Equipment" info on my Nest, it seemed to read the wires incorrectly... Please see below:

    Instead of: Y1-G-Rc-W1-C
    It read as: Y1-C-G-W1-Rc (I think, can double check & get back to you again)

    Any idea what's going on? This is the first time I'm having so much trouble with a Nest thermostat.. The Zone-1 Nest works perfectly, NOT sure what's going on with Zone-2....

    Thank you for the help. Appreciate your time!
    Last edited by maxie.maverick; 06-18-2018 at 09:25 AM.

  4. #10
    Administrator

    User Info Menu

    If you have everything wired correctly the Nest my have a internal issue with the G circuit.

  5. #11
    Junior Member

    User Info Menu

    Quote Originally Posted by Thermostat View Post
    If you have everything wired correctly the Nest my have a internal issue with the G circuit.
    I tried swapping my Nests around and got the same error.. Then I switched the base and still got the same error.

    Something is very weird with the G-wire.

  6. #12
    Member

    User Info Menu

    Assume your G wire is green. Should see if it is a wire issue or a Nest issue since the relay ruled out an NMC-300 issue.
    Swap the yellow and green wires at both ends. If the error changes then it is a wire issue.
    Next try leaving green disconnected at the zone controller and see what Nest error you get. Some zone boards will work without a G by turning it on whenever it sees Y. Otherwise connect Yellow to both Y and G at the NCM-300.
    Lastly, try disconnecting G at the Nest.