Thread: Honeywell RTH9580 thermostat - heating on cooling cycle

  1. #1
    Junior Member

    User Info Menu

    Honeywell RTH9580 thermostat - heating on cooling cycle

    Okay, I give up and need some help with the RTH9580 Honeywell wifi thermostat.

    Installed new thermostat, everything went well, even the wifi. However, when the system goes to 'cool' - it blows hot air.
    -C,R,O,Y,G,W2 wires straight off of old unit and onto new with no issues
    -Confirmed (photo) no errors in labeling wires (previous unit worked)
    -Checked fuses, triple checked wires properly connected
    -Fan works and seems to be controlled by unit
    -Set for forced air, electrical, 1 cooling zone - tried 1 and 2 zones for heating because the W2 wire
    -Put system in 'heat' mode....but in Florida and only goes to 90 degrees when room is 92 ....
    -Honeywell FAQ and troubleshooting pretty thin

    Update Amazon now offers free in home Smart Home Consultation

    I'm at a loss unless it is just a bad unit
    Thanks,
    Eric



  2. #2
    HVAC Thermostat Specialist

    User Info Menu

    Is the condenser (outdoor part) running?


  3. #3
    Junior Member

    User Info Menu

    Yes, and thank you for the response.

  4. #4
    Administrator

    User Info Menu

    Have you tried to change the setup for the reversing valve? If not go to menu > System Setup and switch the setting for "Type of changeover valve"

  5. #5
    Junior Member

    User Info Menu

    I'm having the exact same problem with the exact same wirings. There's no setup option for a changeover valve.

    I tried the heating setting since it's only 88 here and I was still getting warm air.

    these are my before and after pictures.

    Click image for larger version. 

Name:	Honeywell thermostat subase 1.jpg 
Views:	8475 
Size:	88.3 KB 
ID:	904

    Click image for larger version. 

Name:	Honeywell thermostat subase 2.jpg 
Views:	7868 
Size:	94.8 KB 
ID:	905

  6. #6
    Administrator

    User Info Menu

    When you set up the Honeywell RTH9580 did you configure it as a heat pump system?
    When you go to menu > System Setup do you not see a setting for "Type of changeover valve"?

    Looking at your attached picture It looks like the push pin for the W O/B terminal may be damaged.