Originally Posted by
Servicetech
W1 and W2 should each control a sequencer. On a 3 element system each element is typically about 5KW. The 1st 2 elements are typically controlled by the 1st sequencer, and W2 picks up the 3rd element. Most newer air handlers have 2 breakers, 1 for the blower and W1 element(s), the 2nd for W2 element(s) Be sure the 2nd breaker is is getting power. Considering the history of the house it's entirely possible it was hacked and there is no power being fed to the 2nd breaker. If power is good, check the 3rd element for voltage. If no voltage just trace the circuit and see where it's dropping the power.
I think Ecobee is capable of staging W1 and W2, this could keep some of the elements off until they are needed.